I have equipment that can either be ran at 230V single phase or 208VAC single phase. I have a 3KW heating branch within this equipment.
3000W/230V = 13.04A 13.04 * 1.25 = 16A. So for 230V I can use a 20A fuse.
For 208V, the heater Watts derate to around 2.45KW
2.45KW/208 = 11.8A 11.8A * 1.25 = 14.74. So for 208 I can use a 15A fuse.
I would really like to use the 20A fuse for 208 because I am so close to 15A at 1.25 * de-rated current. NFPA 79 is only concerened with heaters above 16.7A.
NEC 424 references me back to 210. I get a little lost here. Is 210 saying that I can use a 15, 20, 30, 40, or 50A OCPD as long as the conductors are rated for this OCPD? Or am I stuck with derating the heaters * 1.25 and then rounding up.