The built-in fuses used to prevent overload in specialized systems are called "Heaters". Is the term "Heaters" a general term or do they have a specific name? If so why are they called "Heaters"?
Although I have them called ?heaters? and in past time called them ?heaters? myself the NEC refers to them as overload devices.430.6(A) (2) Nameplate Values. Separate motor overload protection shall be based on the motor nameplate current rating.
III. Motor and Branch-Circuit Overload Protection
430.31 General.
Part III specifies overload devices intended to protect motors, motor-control apparatus, and motor branch-circuit conductors against excessive heating due to motor overloads and failure to start.
Overload in electrical apparatus is an operating overcurrent that, when it persists for a sufficient length of time, would cause damage or dangerous overheating of the apparatus. It does not include short circuits or ground faults.
100 Overload. Operation of equipment in excess of normal, full-load rating, or of a conductor in excess of rated ampacity that, when it persists for a sufficient length of time, would cause damage or dangerous overheating. A fault, such as a short circuit or ground fault, is not an overload.
Mike I have to disagree.Originally posted by jwelectric:
Although I have them called ?heaters? and in past time called them ?heaters? myself the NEC refers to them as overload devices.