I am going to install some heaters (heater assembly) for a vat. Currently there is a single phase heater being used right now. It is on a 50A circuit with a 50A res/40A fla contactor to open an close the circuit.
The customer ordered a three heater assembly to replace the single unit. Each heater is a 25A single phase unit with the OCP @ 50A according to the tag.
So if I wire them up to a three phase circuit as the wiring diagram shows. (Doing AB, BC, CA which evenly distribute the loads.) I get 6kW * 3 = 18kW
18kW ? 240V 3P = 43.37A
At 125% I get 54A.
So, do I use a 60A breaker and 60A res contactor?
Or, do I follow the single phase ratios and go 75A and 75A?
The customer ordered a three heater assembly to replace the single unit. Each heater is a 25A single phase unit with the OCP @ 50A according to the tag.
So if I wire them up to a three phase circuit as the wiring diagram shows. (Doing AB, BC, CA which evenly distribute the loads.) I get 6kW * 3 = 18kW
18kW ? 240V 3P = 43.37A
At 125% I get 54A.
So, do I use a 60A breaker and 60A res contactor?
Or, do I follow the single phase ratios and go 75A and 75A?