In-house electrical engineer at large national a/c manufacturer is not applying "continuous duty" requirement found in 424.3b. The situation is as follows:
Separate feeder to - 117kw heater at 460v
(117000/360=146.85 1/0 or x 1.25=182a 3/0)
note: the equipment only has terminals for 2/0
1. What is the size of the branch ckt conductor & ocp?
Other issues:
424.22b max 48amp load/ocp60a
2. How many subdivided loads are required?
3. Does the NEC apply to the internal conductors inside
of the heater unit?
4. When can 310.16 column three 90 degree be used?