Heavy Duty or General Duty switches

Status
Not open for further replies.

Woodyz

Member
What are the benifits of Heavy Duty over General Duty,

Higher interupt
Load Make Break
Money?

Looking at for motor disconnect for servicing only not to start and stop.
 
It's more helpful to look at the switches ampre rating and horsepower rating, and pay less attention to what the marketing people might call the switch.
 
IMO a general duty switch would be fine - as (it sounds as if) you would not be generally connecting under load situations. Which would require a much faster acting spring loaded mechanism to snap the contacts into place, and a much higher contact rating. And often will have chambers to contain the initial arc.

In a heavy duty switch, when operating it - you'll notice you are charging a spring, and triggering a release to SLAM the contacts fully shut as fast as possible. In a general duty, (Meant to connect under light/no load conditions) the mechanism will be much slower, and allow a longer time of partial contact. But still must be rated to handle the high amperage of motor starting while closed.

Also, FYI it may be difficult to find a general duty switch rated for over 240V... As over that voltage an arc can be self-sustaining IMO.
 
It is kind of like asking about SO and SJO cords.

Heavy duty switches are normally available up to 600V. They also normally come in more styles of enclosures (like NEMA 7/9) as well as have more accessories.
 
the general duty switch is much cheaper than the heavy duty. comparing the two ,side by side, you can understand why the price difference. two main issues come to my mind when specifying a heavy duty or general duty switch. type of load such as motor loads and how close the maximum load is to the "full load" rating of the switch. an example would be an elevator disconnect. this is a motor load that is continually cycling. if a general duty switch is used and close to the switch's maximum current carrying rating -- it's life of this switch will be shortened. if the load was only 50 per cent of the rating of the general duty switch it may function without a problem. my $.02
 