IMO a general duty switch would be fine - as (it sounds as if) you would not be generally connecting under load situations. Which would require a much faster acting spring loaded mechanism to snap the contacts into place, and a much higher contact rating. And often will have chambers to contain the initial arc.
In a heavy duty switch, when operating it - you'll notice you are charging a spring, and triggering a release to SLAM the contacts fully shut as fast as possible. In a general duty, (Meant to connect under light/no load conditions) the mechanism will be much slower, and allow a longer time of partial contact. But still must be rated to handle the high amperage of motor starting while closed.
Also, FYI it may be difficult to find a general duty switch rated for over 240V... As over that voltage an arc can be self-sustaining IMO.