Re: height of disconnect switch
I am confused about another point. You asked about the height of the disconnect, but then said that the panel itself would be above some ?machine.? So what is above the machine, the panel, the disconnect, or both, or is the disconnect within the panel?
You need to look at 110.26(A)(3). The working space has to be clear from the floor to 6.5 feet above the floor. You can?t put a machine within that space, unless you satisfy that article.
(p.s. I think that Wayne was asking essentially the same question, and has the same concern.)