Have outside AC unit that is hung on wall 10 feet up from ground level.No work platform.Can the disconnect be mounted 10 feet up ?
404.8 Accessibility and Grouping
(A) Location All switches and circuit breakers used as switches shall be located so that they may be operated from a readily accessible place. They shall be installed such that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform.
Exception No. 1: On busway installations, fused switches and circuit breakers shall be permitted to be located at the same level as the busway. Suitable means shall be provided to operate the handle of the device from the floor.
Exception No. 2: Switches and circuit breakers installed adjacent to motors, appliances, or other equipment that they supply shall be permitted to be located higher than 2.0 m (6 ft 7 in.) and to be accessible by portable means.
Jim W in Tampa said:Have outside AC unit that is hung on wall 10 feet up from ground level.No work platform.Can the disconnect be mounted 10 feet up ?