Height of outdoor GFI receptacles

Status
Not open for further replies.

marybeth

Member
What is the minimum height above a concrete slab for a GFI outlet? Can the box itself be plastic while the cover is metal and watertight?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Height of outdoor GFI receptacles

Isn't any. Common sense dictates though that it be above the "high water mark". The box and cover can be any combination also.
 

tonyi

Senior Member
Re: Height of outdoor GFI receptacles

Originally posted by marybeth:
What is the minimum height above a concrete slab for a GFI outlet? Can the box itself be plastic while the cover is metal and watertight?
Squishy words in the code as to minimum height - "accessable at grade level", 6.5' max height. This is for the two required ones.

After the two required recepticals, extras could be just about anywhere. I'll frequently mount one up under the eaves for things like christmas lights and bug zappers so people don't have to run lead cords out windows and doors and other dangerous stuff like that...

Did someone stick one almost in the dirt on you?
 
A

a.wayne3@verizon.net

Guest
Re: Height of outdoor GFI receptacles

I once did a service call(w.p. gfi tripping) I went thru the circuit in the house and traced the problem to where it exited the home through a bell box to an underground conduit.What i found was a pvc floor box in the middle of the yard, previous homeowner set up christmas displays and didnt want to run cords or run over a receptacle with the lawn mower so he installed a floor box and receptacle in the ground.It had rained for 3 weeks straight and the box filled with water.DIY
strikes again.
 

pierre

Senior Member
Re: Height of outdoor GFI receptacles

Welcome Marybeth

It is nice to see another woman posting here.
Your question is actually quite common. As the others have stated, for your question, there is no minimum height requirement.
If you are in an area where snow can pile up or the water tends to rise, you can advise the customer and plug away. :D

Pierre
 