If triplex (or quadplex) is used to feed a detached garage, what is the height requirement ? 225.18 (1) says 10' for 150v, but what is it for 240 v ? 12' as it says in (2) ? So 12 ' ? Thank you
the exact same requirements as 230.22 for service conductors ?
 
If triplex (or quadplex) is used to feed a detached garage, what is the height requirement ? 225.18 (1) says 10' for 150v, but what is it for 240 v ? 12' as it says in (2) ? So 12 ' ? Thank you
the exact same requirements as 230.22 for service conductors ?
225.18 (1) says 10' for 150v, ----

No, it states if the conductors don't exceed 150 to GROUND not between conductors. So the height is for 240v also
 