height of subpanel ?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Is there a specified height for a sub panel in a home? When we add a sub panel close to a house panel, sometimes the easiest place is right below the main panel. But is that too low? I always put it beside the panel, but that is more work to do. Thank you.
 
Does it make any difference if this panel is in a garage?
No. The rules for this don't matter if it is dwelling or not either. I have installed panels that go in ~7 foot tall cabinet. I believe it was 54 space NF panel with 400 amp main breaker, as well as some I-Line panels. In order to keep the highest handle below the maximum allowed height the bottom of the cabinet has to be pretty low.
 