Hello, as the title states, I am a mechanical engineer that has been thrust into an electrical engineers position for a short time while we look for another to replace ours.
My question/issue is that I am testing thermal rise in a copper bus system by loading current and shorting out the opposite end of the bus system, it is 3 phase bus and I have a 3 phase current generator that can output 4000 amps at 24 volts. Testing a simple bus run is pretty straight forward, I short one end and place thermocouples along the bus in the manner prescribed by UL to measure the temperature rise...simple stuff even for a mechanical engineer! However, I have been thrown for a big loop in that I now have a main horizontal bus system that is rated at 3200 amps and connected to it is a vertical bus system that is rated at 800 amps. The joint between these two bus systems is where I need to check temperature rise. I short the horizontal bus system, like always (now the tough part) and put an 800 amp load on the vertical section. That should give me 2400 amps in the horizontal and 800 in the vertical. Problem is, how do I load the vertical bus? A solid short only puts around 250 amps of load. I added lengths of wire to the end of the vertical bus to add resistance, 3 pieces per phase of 350 MCM @ 12 feet lengths. That number was given to me by the guy that retired. When I started the generator, I actually got LESS resistance in the vertical down to 120 amps. That just doesn't seem right...
What if I add a steel bar instead of the copper bar that is used to short the vertical, steel has +/- 10 times the resistance as copper, so that should just act as a 19,200 watt heater? All I would need to do is calculate the required size of steel, I think.
Any other ideas? Remember, like most companies, I can't spend any money on this...I'm sure you all know how that goes.
Thanks
My question/issue is that I am testing thermal rise in a copper bus system by loading current and shorting out the opposite end of the bus system, it is 3 phase bus and I have a 3 phase current generator that can output 4000 amps at 24 volts. Testing a simple bus run is pretty straight forward, I short one end and place thermocouples along the bus in the manner prescribed by UL to measure the temperature rise...simple stuff even for a mechanical engineer! However, I have been thrown for a big loop in that I now have a main horizontal bus system that is rated at 3200 amps and connected to it is a vertical bus system that is rated at 800 amps. The joint between these two bus systems is where I need to check temperature rise. I short the horizontal bus system, like always (now the tough part) and put an 800 amp load on the vertical section. That should give me 2400 amps in the horizontal and 800 in the vertical. Problem is, how do I load the vertical bus? A solid short only puts around 250 amps of load. I added lengths of wire to the end of the vertical bus to add resistance, 3 pieces per phase of 350 MCM @ 12 feet lengths. That number was given to me by the guy that retired. When I started the generator, I actually got LESS resistance in the vertical down to 120 amps. That just doesn't seem right...
What if I add a steel bar instead of the copper bar that is used to short the vertical, steel has +/- 10 times the resistance as copper, so that should just act as a 19,200 watt heater? All I would need to do is calculate the required size of steel, I think.
Any other ideas? Remember, like most companies, I can't spend any money on this...I'm sure you all know how that goes.
Thanks