Actually, I want to get a better understanding of both the service load calculations and the branch circuit sizing calculations.
Service is 208Y/120V. This is what I have from the equipment specs:
Undercounter refrigerator:
Undercounter ice maker:
I'd like to place both of these on a single branch circuit (one duplex GFCI receptacle).
My question about the service loads has to do with the ice maker having a 1/4 HP rating but also 10A rating. From NEC Table 430.248, the FLC for a 1/4 HP motor is 5.8A. But I assume that since the manufacturer's specified current rating is higher, I should use the 10A value. For the refrigerator, the Table 430.248 FLC is 4.4A based on 1/6 HP (and ignoring the 2A rating by the manufactuer).
So for the refrigerator, Load = 120V x 4.4A = 528 VA
And for the ice maker, Load = 120V x 10A = 1,200 VA
Is this correct so far?
Now the branch circuit conductor and OCPD sizing is where I'm really confused. Article 440 really kicks you around all over the NEC. For example, Section 440.3(C) sends you to Article 422. Section 422.11(G) sends you back to Part VI of Article 440. Section 440.51 of Article 440 Part VI has a FPN referring you back to 240.4(G) for application of Parts III and VI of Article 440. Section 240.4(G) states that for air conditioning and refrigeration equipment conductors, to reference Article 440, Parts III, VI. (Ok, now I'm getting dizzy.)
440.22(A), it states that "A protective device having a rating or setting not exceeding 175 percent of the motor compressor rated-load current or branch-circuit selection current, whichever is greater, shall be permitted."
Is rated-load current the equipment's amperage rating from the manufacturer or the FLC from Table 430.428?
And what about the "branch-circuit selection current"? Part of the problem I have with Article 440 is that a lot of it seems to rely on the nameplate markings on the equipment itself. But how is one to design the electrical system before the equipment is acquired? As I read 440.4(C), the branch-circuit selection current appears to be based on what's printed on the nameplate (which is omitted from equipment spec sheets). Section 440.12 also requires the nameplate data.
So now I'm completely befuddled as to how to determine the branch circuit ampacity and OCPD for the refrigerator and ice maker listed above. My gut instinct tells me these these two should run just fine on a 20A/12AWG circuit (but with a 15A OCPD due to the ice maker's MOCP restriction). But I really would like to understand how to work though all the twists and turns of calculating the correct wire ampacity and OCPD values.
Could someone please help walk me through this?
Service is 208Y/120V. This is what I have from the equipment specs:
Undercounter refrigerator:
115V, 1-phase, 2A, 1/6 HP, NEMA 5-15 plug
Undercounter ice maker:
115V, 1-phase, 10A, 1/4 HP, MOCP 15A, NEMA 5-15 plug
I'd like to place both of these on a single branch circuit (one duplex GFCI receptacle).
My question about the service loads has to do with the ice maker having a 1/4 HP rating but also 10A rating. From NEC Table 430.248, the FLC for a 1/4 HP motor is 5.8A. But I assume that since the manufacturer's specified current rating is higher, I should use the 10A value. For the refrigerator, the Table 430.248 FLC is 4.4A based on 1/6 HP (and ignoring the 2A rating by the manufactuer).
So for the refrigerator, Load = 120V x 4.4A = 528 VA
And for the ice maker, Load = 120V x 10A = 1,200 VA
Is this correct so far?
Now the branch circuit conductor and OCPD sizing is where I'm really confused. Article 440 really kicks you around all over the NEC. For example, Section 440.3(C) sends you to Article 422. Section 422.11(G) sends you back to Part VI of Article 440. Section 440.51 of Article 440 Part VI has a FPN referring you back to 240.4(G) for application of Parts III and VI of Article 440. Section 240.4(G) states that for air conditioning and refrigeration equipment conductors, to reference Article 440, Parts III, VI. (Ok, now I'm getting dizzy.)
440.22(A), it states that "A protective device having a rating or setting not exceeding 175 percent of the motor compressor rated-load current or branch-circuit selection current, whichever is greater, shall be permitted."
Is rated-load current the equipment's amperage rating from the manufacturer or the FLC from Table 430.428?
And what about the "branch-circuit selection current"? Part of the problem I have with Article 440 is that a lot of it seems to rely on the nameplate markings on the equipment itself. But how is one to design the electrical system before the equipment is acquired? As I read 440.4(C), the branch-circuit selection current appears to be based on what's printed on the nameplate (which is omitted from equipment spec sheets). Section 440.12 also requires the nameplate data.
So now I'm completely befuddled as to how to determine the branch circuit ampacity and OCPD for the refrigerator and ice maker listed above. My gut instinct tells me these these two should run just fine on a 20A/12AWG circuit (but with a 15A OCPD due to the ice maker's MOCP restriction). But I really would like to understand how to work though all the twists and turns of calculating the correct wire ampacity and OCPD values.
Could someone please help walk me through this?