Hi,
I'm designing a control panel for a new assembly line. We have some 240V equipment, all singe phase except for one unit, which is 3 phase. We decided it'd be best to use a 480/240 3 phase transformer and feed all our single phase and our one 3 phase pieces of equipment with the one transformer instead of having multiple transformers floating around the assembly line.
However, since our single phase equipment is split between different legs of the 3 phase secondary side, with the addition of the 3 phase unit obviously tied to all 3 phases, I'm not sure how to calculate what the actual load would be in order to properly fuse the secondary side of the transformer and also size the wire coming into the distribution block. I was told that since it's 3 phase output, but for certain parts we are only using 1 phase, that I can't just added up all the sums, and that loads need to be moderately balanced between different phases.
I'm attaching screenshots of my AutoCAD Electrical drawing. Some notes in case the font is too small......
I appreciate any advice or help you guys can offer for this.
EDIT: The screenshots are really small. Not sure why they got shrunk. Added more detail to compensate.
I'm designing a control panel for a new assembly line. We have some 240V equipment, all singe phase except for one unit, which is 3 phase. We decided it'd be best to use a 480/240 3 phase transformer and feed all our single phase and our one 3 phase pieces of equipment with the one transformer instead of having multiple transformers floating around the assembly line.
However, since our single phase equipment is split between different legs of the 3 phase secondary side, with the addition of the 3 phase unit obviously tied to all 3 phases, I'm not sure how to calculate what the actual load would be in order to properly fuse the secondary side of the transformer and also size the wire coming into the distribution block. I was told that since it's 3 phase output, but for certain parts we are only using 1 phase, that I can't just added up all the sums, and that loads need to be moderately balanced between different phases.
I'm attaching screenshots of my AutoCAD Electrical drawing. Some notes in case the font is too small......
- 240V 1 Phase - Hot Melt Pump 1 = 35A fuses (Fed from secondary phases L1-L2)
- 240V 1 Phase - Hot Melt Pump 2 = 35A fuses (Fed from secondary phases L1-L3)
- 240V 1 Phase - Hot Melt Control Unit = 20A fuses (Fed from secondary phases L2-L3)
- 240V 1 Phase - Nordson Pump = 12A fuses(Fed from secondary phases L2-L3)
- 240V 3 Phase - Nordson Control Unit = 15A fuses (Fed from secondary phases L1-L2-L3)
I appreciate any advice or help you guys can offer for this.
EDIT: The screenshots are really small. Not sure why they got shrunk. Added more detail to compensate.