Help - Code Reference for Line Side Terminals on Top

Status
Not open for further replies.

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
All,

Too early for full brain function. I believe there is a Code rule for the upper terminals in a disconnect to be the Line Side Terminals. Does anyone remember which Article this is?

As always, thanks and happy Thursday.

Mark
 

busman

Senior Member
Location
Northern Virginia
Occupation
Master Electrician / Electrical Engineer
I think I answered my own question by Googling old Mike Holt threads. Only a requirement if the CB is marked Line and Load OR knife switches depending on orientation. Did I get this right?

Thanks

Mark
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
FYI, and jim can correct me if this is wrong, but I think your references would be 404.6 for the switch and 110.3(b) for the breaker.
 