We've been troubleshooting a vessel used for heating parts. It uses a DC power supply to provide 45 V at 8000 A. We continue to get a sporadic DC over current fault identified by a mV reference from the negative bus. I recently removed the leads from the power supply to attempt testing the load side isolation to ground as it should be isolated. Using an Ohmmeter I get around 1400+ Ω between each zone to ground. Using our megger set at 50 V, I get 0 MΩ which would lead me to believe that I have bad insulation somewhere in the circuit. How can I explain to our non electrical engineers the difference in these readings, because if I tell them that my resistance reading is showing 1400+, but my insulation reading is 0, they're going to be confused because they are both an Ω measurement.