Does anyone know what article requires you to not put more than 80% of a breakers rating load on the breaker. for example a 20A breaker would only be allowed to be designed for 16A above and beyond the whole continuous load 125%
The 80% you are talking about is the same as the 125% rule. If you take a 16 amp circuit and apply the 125% rule you will get 20 amps. If you reverse this and apply 80% to the 20 amp circuit you will get 16 amps.
so to that end that would mean that if I have a panelboard that has a 100A of feeder demand load on it then I can size the main breaker on that panel for 100A? I thought I would have to size that breaker for 125A for a safety factor.