Help Finding Code Article

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'm trying to find the section concerning conductors in conduit that enter the top of a panel and are not required to be derated if the conduit is not over a certain length. I found where a nipple not exceeding 24" is not counted, but that is not what I'm looking for. I'm probably blind, but I can't seem to find what I'm looking for!
 
I admit, I never saw the connection. Nice Job

Com'on Jumper, get with the program!:p

Although the article itself doesn't say anything about derating, it kind of goes along with it provided the section of conduit doesn't exceed 24".

I'm used to looking in the handbook if I can't find it on my computer. The handbook mentions that if the raceway doesn't exceed 24" it doesn't have to be derated.
I had remembered seeing that and that is why I asked the question the way I did.

Well not really the only reason I asked it the way I did. I was in an extreme hurry when I posted, and that's what came out when I typed it!:)
 