I hired an electrician to install an electrical connection to a water well that will be drilled in the next two weeks. Unfortunately I now understand what I got was a non-code compliant, potentially unsafe installation. I am looking for advice on the best way to correct what I have now so that it is safe and to code. The diagram shows the current installation.
The wire used is 2-2-4 USE-2 XLP Aluminum. The last 70 feet of the run to the service entrance is through my attic. The balance is underground in a still open trench.
The problems I know of are; the wire should have been four conductor instead of three. The ground should not be connected to neutral at the remote box. The attic run should have been in conduit. The wire may not be suitable for indoor use at all even in conduit?
My possible options seem to be:
1. Rip it all out and replace the entire run with #6 3-wire with ground UF-B copper ($$$)
2. Add single #2 AL wire or single #6 Copper for entire run, add conduit in attic. Switch present neutral wire to ground. Use the new wire for the neutral connection. Problem with this is it is hard to find single conductor direct burial wire. Maybe buy more 3 wire - strip it apart and put in splices??
3. Rip it all out and replace the entire run with 2-2-2-4 USE-2 XLP Aluminum. Add conduit in attic. Won't work if this wire can't be used in indoors.
4. Add #8 or #6 bare copper wire for ground connection. Add conduit in attic.
5. Add box where the run enters the attic on the well pump side and switch to suitable indoor wire as necessary. Run a fourth wire to the remote box for the added ground.
6. Combinations of the above?
Obviously I don't want to spend any more money/time than necessary but I also want a safe and compliant installation.
All comments and suggestions are very welcome.

The wire used is 2-2-4 USE-2 XLP Aluminum. The last 70 feet of the run to the service entrance is through my attic. The balance is underground in a still open trench.
The problems I know of are; the wire should have been four conductor instead of three. The ground should not be connected to neutral at the remote box. The attic run should have been in conduit. The wire may not be suitable for indoor use at all even in conduit?
My possible options seem to be:
1. Rip it all out and replace the entire run with #6 3-wire with ground UF-B copper ($$$)
2. Add single #2 AL wire or single #6 Copper for entire run, add conduit in attic. Switch present neutral wire to ground. Use the new wire for the neutral connection. Problem with this is it is hard to find single conductor direct burial wire. Maybe buy more 3 wire - strip it apart and put in splices??
3. Rip it all out and replace the entire run with 2-2-2-4 USE-2 XLP Aluminum. Add conduit in attic. Won't work if this wire can't be used in indoors.
4. Add #8 or #6 bare copper wire for ground connection. Add conduit in attic.
5. Add box where the run enters the attic on the well pump side and switch to suitable indoor wire as necessary. Run a fourth wire to the remote box for the added ground.
6. Combinations of the above?
Obviously I don't want to spend any more money/time than necessary but I also want a safe and compliant installation.
All comments and suggestions are very welcome.