Help> Generator Sizing .?

Status
Not open for further replies.

Nxtu

Member
Hi everyone ,
I have 3 phase load==> about 350 amp I'll using 480 volts 60 Hz
The Load > 3 phase AC Motors + A/C + Lighting
the question is what is the suitable size of generator (KW) i need ?
thanks
 
Last edited:
Contact a a few Generator manufacturers, you will need to tell them the size of all motors, how many may start at once, heat/AC load, the type of fuel you intend to use, altitude, and some other specifics, they will be able to tell you.

Roger
 
Also let them know if any of the load is a UPS load.
This effects the generator is there is not enough resistive load on it.
 