I'm looking for a little assistance with identifying the code violations visible in the images below. One of our estimators is working on a quote to replace these panelboards, but they feel there are multiple violations that they have asked me to help identify. The concerns they mentioned were wire coloring, lack of chase nipples, and the FMC running through the panel.
So far, I've only been able to identify two solid code violations:
Does anyone disagree with either of these violations?
Next, looking at the lack of chase nipples between panels, this seems like it should be a violation of 300.4(G). However, since 300.4(G) states, "Where raceways contain..." it seems that this code wouldn't be applicable here since there's no raceway. So, is the lack of chase nipples a code violation?
Next, looking at the FMC that runs through the panel on the right. Does anyone know of a code this violates? As odd as it looks, I haven't been able to find any code that prohibits a raceway from running though a cabinet.
Lastly, do you notice any other NEC violations that I'm missing? Thanks in advance!



So far, I've only been able to identify two solid code violations:
- Center panelboard has red and black conductors landed on ground bus. Violation of 250.119; equipment grounding conductors 6 AWG or smaller must be bare, green, or green with one or more yellow stripes.
- Center panelboard has feed-through conductors. Assuming there is no warning label on the panel to identify the nearest disconnecting means for these conductor, this is a violation of 312.8. Same goes for the circuit in the FMC running though the panel on the right.
Does anyone disagree with either of these violations?
Next, looking at the lack of chase nipples between panels, this seems like it should be a violation of 300.4(G). However, since 300.4(G) states, "Where raceways contain..." it seems that this code wouldn't be applicable here since there's no raceway. So, is the lack of chase nipples a code violation?
Next, looking at the FMC that runs through the panel on the right. Does anyone know of a code this violates? As odd as it looks, I haven't been able to find any code that prohibits a raceway from running though a cabinet.
Lastly, do you notice any other NEC violations that I'm missing? Thanks in advance!