I been called to install additional circuits in a commercial building.
I’m having trouble deciding what the construction classification is.It’s a stick built structure with exterior metal siding and interior finished drywall walls and ceilings.
The attic space where I need to route new circuits through is open wood truss. Past work is all NM cable across and stapled to the side of the trusses and then dropped down in AC cable to either equipment or receptacles.
Since it’s a local job I know that major renovation took place there recently and was permitted through the township.
Im seeing the prior work as not code compliant since it lacks a 15 minute barrier as it’s exposed in the trusses space.
Am I wrong in my thinking?
Thank you.