dlukert
Member
- Location
- San Antonio, TX
- Occupation
- Electrical Engineer
I have recently encountered this requirement that I was unaware of and am having trouble understanding the intent and how it should apply to most buildings. I can think of several buildings I've designed or been in myself, that do not seem to comply with this requirement. The way I read this code, you can't even lock an electrical room with branch circuits, except in specific instances (guest rooms and dorms). Can someone help me understand where I'm going wrong here?
From 2023 NEC:
240.24(B) Occupancy.
Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy, unless otherwise permitted in 240.24(B)(1) and (B)(2).
(1) Service and Feeder Overcurrent Protective Devices.
(2) Branch-Circuit Overcurrent Protective Devices.
Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the branch-circuit overcurrent protective devices supplying any guest rooms, guest suites, or sleeping rooms in dormitory units without permanent provisions for cooking shall be permitted to be accessible only to authorized management personnel.
How would a commercial office building comply with this? They generally use common electrical rooms and restrict access to tenants in my experience. Some in my office have pointed to 240.24(B)(1), but this only applies to service and feeder OCPDs, not branch circuits.
It seems obvious that this shouldn't apply to a school, daycare or other occupancy with children, or even more obvious would be something like a prison, but there are no exceptions that I can see.
From 2023 NEC:
240.24(B) Occupancy.
Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy, unless otherwise permitted in 240.24(B)(1) and (B)(2).
(1) Service and Feeder Overcurrent Protective Devices.
(2) Branch-Circuit Overcurrent Protective Devices.
Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the branch-circuit overcurrent protective devices supplying any guest rooms, guest suites, or sleeping rooms in dormitory units without permanent provisions for cooking shall be permitted to be accessible only to authorized management personnel.
How would a commercial office building comply with this? They generally use common electrical rooms and restrict access to tenants in my experience. Some in my office have pointed to 240.24(B)(1), but this only applies to service and feeder OCPDs, not branch circuits.
It seems obvious that this shouldn't apply to a school, daycare or other occupancy with children, or even more obvious would be something like a prison, but there are no exceptions that I can see.