I will be submitting (2) changes to article 680.74 for the next cycle and would like your thoughts/opinions on my proposals.
(1) Remove the first sentance of 680.74 and replace it with the following (change in bold) All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together with a solid bonding jumper , insulated, covered or bare, not smaller than #8 AWG.
Substantiation to #1: If the intent of the code is that a solid conductor is to be used, the existing code text is not enforcible. To state that the bonding jumper is to be not smaller than #8 AWG solid would permit a stranded conductor larger than #8 AWG to be used.
(2) Remove the first sentance of 680.74 and replace it with the following (change in bold) All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together with a bonding jumper, insulated, covered or bare, not smaller than #8 AWG.
Substantiation to #2: If the intent of the code is that a stranded conductor may be used, there is no reason to include the word "solid" in this article.
[ October 13, 2003, 07:25 PM: Message edited by: ryan_618 ]
(1) Remove the first sentance of 680.74 and replace it with the following (change in bold) All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together with a solid bonding jumper , insulated, covered or bare, not smaller than #8 AWG.
Substantiation to #1: If the intent of the code is that a solid conductor is to be used, the existing code text is not enforcible. To state that the bonding jumper is to be not smaller than #8 AWG solid would permit a stranded conductor larger than #8 AWG to be used.
(2) Remove the first sentance of 680.74 and replace it with the following (change in bold) All metal piping systems, metal parts of electrical equipment, and pump motors associated with the hydromassage tub shall be bonded together with a bonding jumper, insulated, covered or bare, not smaller than #8 AWG.
Substantiation to #2: If the intent of the code is that a stranded conductor may be used, there is no reason to include the word "solid" in this article.
[ October 13, 2003, 07:25 PM: Message edited by: ryan_618 ]