Years ago when replacing some switchboard meters the guy I was working with had some clips you could use to short out the CT's if there was not a shorting block installed.

They looked kind of like test leads only the spring loaded ends would actually pierce the insulation of the CT leads. Made a very small cut/piercing. You clipped one end to the + lead and one to the - or common if it was a wye and shorted the CT out so you could replace the meter or install permanent shorting blocks.

I need a set of these clips but cannot find them anywhere.

Anyone know what I'm talking about and know where to get them or even what they are called?
 

bbaumer

Senior Member
Location
Indiana
Aha! Found it. Sorry.

http://us.fluke.com/usen/products/AccessoryDetail.htm?cs_id=204(FlukeProducts)&catalog_name=FlukeUnitedStates

ac89_main.jpg
 

djohns6

Senior Member
Location
Louisiana
I highly recommend that you NOT use that device to short out a current circuit . If you have ever witnessed an open CT , you wouldn't ask why .
Find another , safer way to short out the circuit prior to opening it .
 

danickstr

Senior Member
how high is the voltage/current on the primary your CT is on?

If there is a lot of power current going through it, it will act as a transforming channeler of sorts and could shoot a lot of impeded VA's
 
Last edited:

bbaumer

Senior Member
Location
Indiana
First off, yes I have opened the secondary of a CT before a couple of times. Once out of ignorance years ago and once by accident.

Yes, it drew an arc and made me jump. Something about a current source through an infinite resistance creates an infinite voltage. Well, not really but the whole Ohms law thing applies, hence the high voltage arc. Buzzed really loud too as I recall.

Second, the maximum current flowing/circulating through the leads when shorted is 5A due to the CT ratio.

I installed/helped install some 70+ meters at this site years ago and am being called on now to replace one. All the switchboards at this campus have 800:5, 1600:5, 2000:5 etc. CT's depending on the size of the board. Most boards are very lightly loaded as compared to their rated capacity. Ex. 2000A board may have 400-600A on it. With a 2000:5 CT that would only be about 1.2 to 1.5A on the CT secondary. These clips can handle that easily and are rated for it.
 
Last edited:

djohns6

Senior Member
Location
Louisiana
I'm not concerned with wether the clip can carry the current , but rather , the method of piercing the insulation and making a secure connection .
There are NO shorting blocks ANYWHERE in the circuit ?
 

bbaumer

Senior Member
Location
Indiana
I'm not concerned with wether the clip can carry the current , but rather , the method of piercing the insulation and making a secure connection .
There are NO shorting blocks ANYWHERE in the circuit ?

No. I could swear we added them everywhere that did not have them on the first go 'round 9 or 10 years ago but lo and behold none on this board. There is a terminal block but it is just that, a terminal block. Not a shorting block.

I have a few of options.

1. Shut the board down and go to work.
2. Short out using the clips and immediately install jumpers on the terminal block to create a safer condition.
3. Attempt to loosen the screws on the terminal block and install jumpers and hope not to open one of the CT secondary circuits. I think this is a slim chance and not as safe as using the clips.

Shutting the board down is possible but would be a major disruption for the Owner. I think they would go without metering before they would do this.
 

jdsmith

Senior Member
Location
Ohio
Option two sounds pretty reasonable . Use a wire jumper with forked " sta-kons " . Just loosen the screw and slide it under . :)

I would choose option 2a - short out using the clips, install shorting blocks, and re-terminate CT wiring on proper shorting blocks. I just priced the blocks yesterday - $27 is a pretty cheap one-time cost to avoid having to go through that risky maneuver more than once.
 