bullheimer
Senior Member
- Location
- WA
i am figuring $10/ft. this is only $600 which doesnt seem like enough for me. breakers are $100 so add that to it. =$700, but still, the run is on the ceiling and half of the run is above a drop ceiling. if i figure 5 hours at $75/hr its only $375, plus $75 wire, $70 pipe $10 fittings, $40 recept. $100 breaker, or $670. (those prices have no mark up. so with 25% on top of the material, = $370, 370+375 is $750. pretty much the same as the $10/ft thing, just doesnt seem like i will make enough profit to justify the day there. i have two runs to do i could do them in one day so i would make $750 for the day. i want to make at least $850 for ONE. which would be$1250 for the first one.
think $1250 for one run of 1" and $1000 for 1 run of 3/4" is gouging? (above materials were #8 wire and 1" emt.) that would be $2250 total for 3 30A three phase recepts.
what he wants is one room with a 30A twist to lock 3 phase, and another room with two 30 recepts.
can i just take one set of #8wires to a j-box to the room that wants two recepts and drop #10's down to the recepts? the ampacities on the equipment is @15A each. or would i have to install #6 (or bigger) to get 60A that could theoretically be hooked up to the two 30A recepts by somebody in the future? (the equipment comes with the 30A cord caps).
just as a sidebar, i can never figure out how this fusing thing applies to feeders with taps. i would be using a 50A breaker on the #6, so that means the #10 is protected by a 50A fuse, which ordinarily you can't do, so how is that okay when you are talking about taps, but not other kinds of wiring?
think $1250 for one run of 1" and $1000 for 1 run of 3/4" is gouging? (above materials were #8 wire and 1" emt.) that would be $2250 total for 3 30A three phase recepts.
what he wants is one room with a 30A twist to lock 3 phase, and another room with two 30 recepts.
can i just take one set of #8wires to a j-box to the room that wants two recepts and drop #10's down to the recepts? the ampacities on the equipment is @15A each. or would i have to install #6 (or bigger) to get 60A that could theoretically be hooked up to the two 30A recepts by somebody in the future? (the equipment comes with the 30A cord caps).
just as a sidebar, i can never figure out how this fusing thing applies to feeders with taps. i would be using a 50A breaker on the #6, so that means the #10 is protected by a 50A fuse, which ordinarily you can't do, so how is that okay when you are talking about taps, but not other kinds of wiring?