ROBOJOE77
Member
- Location
- troutdale oregon
- Occupation
- manufacturing plant journeyman
Our facility has a project underway requiring (3) variable reactance power supplies which themselves require an 800 Amp breaker for each power supply. Our company has hired an outside engineering firm who is now trying to figure out where they are going to pull power from now that we're 8 months into the project who states, their exact words, "We originally approached the design using one of the 1200A breakers with a distribution or termination box splitting into the three 800A connections to the power supplies". This is a pre-existing unused 1200 Amp breaker at one of our MDP's. Can somebody explain to me how this works? These are 250 kVA power supplies @ 480VAC single phase = 521 Amps x 125% = 651.25 Amps each. How do you put this kind of load on a main distribution breaker of 1200 Amps? I'm no engineer, merely a 3rd year Plant Journeyman, but this doesn't seem to math out.