Ok, so here's the back story, There is an existing setup in an electrical room in a plant I'm working on...400amp breaker at main switchgear, running 500mcm to a 225 kva XFMR (480 to 208 running in reverse) a 200amp fusible disconnect after the XFMR that powers the large air compressor for the plant.
So apparently everything has worked for more than a year...they recently had problems with the air compressor and the air compressor tech comes in to work on it and it has an error code in the compressor that says "over amperage" (on the variable drive...) Compressor tech cries bad transformer. No tripped breakers, no blown fuses, and manufacturer spec is 200amp fuse. He recorded voltage readings line to line and found 470,480,510. So before I got involved the transformer was changed to a different brand and type but same specs...once transformer was swapped they tried to turn the breaker on but it wouldn't reengage, so they swapped the breaker with a brand new one....
Then I come in. I took feeders off breaker and transformer and megged phase to ground and phase to phase 4,000+ megs on each so I'm good there. Then megged directly to conduit in case it wasnt grounded sufficiently still 4,000+megs...turned disconnect off on secondary. Megged everything on secondary side. Good there. Checked transformer wiring. Everything looks good to me there (it was tapped for 468, so I did change taps to provide 480) I tried to reengage breaker with no load on transformer and it tripped instantly twice. Since I was sure nothing was direct shorting I assumed I was dealing with Inrush (something I admittedly have a hard time understanding completely, given all the variables and misinformation)
so I cycled the breaker a 3rd time and I had an amprobe on 1 leg and the amp meter reading a different phase on switchgear (rest of plant is dead, so it's only reading our transformer setup) the breaker did not trip instantly, and instead for ~10 seconds there was transformer noise and both my amprobe (1,000 amp limit) and the amp meter (2,000amp limit) were maxed, I waited for Inrush to settle and feel as though I waited ample time, after the 10seconds I tripped the breaker manually, for fear it wasn't going to trip, and amp meters we're still maxxed.
So here is my question. What exactly is the diagnosis? It's been working for over a year with this setup and I know for a fact this plant has been through 3 outages in that year....So do I diagnose a faulty transformer? That's the only thing that's really changed...and That's what I believe....but my knowledge on inrush is limited, and I have no clue if Inrush could last that long under certain circumstances. And if it does is it normal? In my experience less than a second it's usually over, and if the breaker trips instantly, you cycle the breaker a few times hoping to hit it at the right phase angle....
Help me understand what I don't. Is it simple? Is it just a bad transformer? Or Am I missing something? Can inrush last such a long time? Where do I go from here?
So apparently everything has worked for more than a year...they recently had problems with the air compressor and the air compressor tech comes in to work on it and it has an error code in the compressor that says "over amperage" (on the variable drive...) Compressor tech cries bad transformer. No tripped breakers, no blown fuses, and manufacturer spec is 200amp fuse. He recorded voltage readings line to line and found 470,480,510. So before I got involved the transformer was changed to a different brand and type but same specs...once transformer was swapped they tried to turn the breaker on but it wouldn't reengage, so they swapped the breaker with a brand new one....
Then I come in. I took feeders off breaker and transformer and megged phase to ground and phase to phase 4,000+ megs on each so I'm good there. Then megged directly to conduit in case it wasnt grounded sufficiently still 4,000+megs...turned disconnect off on secondary. Megged everything on secondary side. Good there. Checked transformer wiring. Everything looks good to me there (it was tapped for 468, so I did change taps to provide 480) I tried to reengage breaker with no load on transformer and it tripped instantly twice. Since I was sure nothing was direct shorting I assumed I was dealing with Inrush (something I admittedly have a hard time understanding completely, given all the variables and misinformation)
so I cycled the breaker a 3rd time and I had an amprobe on 1 leg and the amp meter reading a different phase on switchgear (rest of plant is dead, so it's only reading our transformer setup) the breaker did not trip instantly, and instead for ~10 seconds there was transformer noise and both my amprobe (1,000 amp limit) and the amp meter (2,000amp limit) were maxed, I waited for Inrush to settle and feel as though I waited ample time, after the 10seconds I tripped the breaker manually, for fear it wasn't going to trip, and amp meters we're still maxxed.
So here is my question. What exactly is the diagnosis? It's been working for over a year with this setup and I know for a fact this plant has been through 3 outages in that year....So do I diagnose a faulty transformer? That's the only thing that's really changed...and That's what I believe....but my knowledge on inrush is limited, and I have no clue if Inrush could last that long under certain circumstances. And if it does is it normal? In my experience less than a second it's usually over, and if the breaker trips instantly, you cycle the breaker a few times hoping to hit it at the right phase angle....
Help me understand what I don't. Is it simple? Is it just a bad transformer? Or Am I missing something? Can inrush last such a long time? Where do I go from here?