Help on cooking equipment???

Status
Not open for further replies.
Looking at a commercial grill, its a 3 phase 12kw 208 cooking unit says the name plate and spec. sheet. Looking at the specs it calls for a MINIUMUM of a #6 copper for the supply (on at least 2 of the phases, the 3rd phase you can use minimum of #8). When I did the math, I came up with

12,000/(208*1.73)=33.35 amps

which means that #8 copper should work for all 3 phases. But like I said, it calls for A phase=#6 copper, B phase=#6 copper, C phase=#8 copper.

Also on the spec. sheets it shows 38.2 amps on A phase, 38.2 on B phase, and 25 amps on C phase. I thought that was odd since the nomeclature shows it as a 12kw 208 3 phase cooking unit. Not sure where the extra amps comming from. And no, its not a continous load. Am I missing something here?? Thanks for the help.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Your math assumes the 12kw is evenly porprtioned between all three phases, where, in fact, it probabnly is not.
A lot of that equipmemt is designed so it can work on single phase also and may be split into 4 heat banks instead of 3.
 