Hello,
We are building a piece of outdoor equipment that will be enclosed in a metal industrial cabinet.
We have a 220V loadcenter attached to the cabinet to supply the power for the equipment.
The supplied power is three wires, Hot-Hot-Ground.
The loadcenter has several 220V GFCI Schneider Electric QO breakers we put in as a safety measure.
One of these breakers is used exclusively to power an APC UPS, which we used to provide the power to our electronics equipment (computer, data acquisition electronics, sensors, etc.).
All of our equipment is DC powered, we use commercial power supplies to convert the AC to DC.
the only AC equipment is an air blower, which is on it's own branch with a GFCI breaker.
The cabinet and all of the equipment is grounded.
There are no external outlets.
We have a problem with the UPS, it is tripping the GFCI breaker when the UPS output power is off (battery discharged or intentionally disable output power).
We contacted APC and were told that the UPS exhibits leakage currents as a result of the common mode filters present within the UPS and the equipment connected to it.
We are now questioning ourselves about the need to have the GFCI breaker for the UPS, or just replace it with a regular breaker.
I've been reading the electric code and could not find a definitive answer.
I'm hoping to gain insight from your comments. Thank you.
We are building a piece of outdoor equipment that will be enclosed in a metal industrial cabinet.
We have a 220V loadcenter attached to the cabinet to supply the power for the equipment.
The supplied power is three wires, Hot-Hot-Ground.
The loadcenter has several 220V GFCI Schneider Electric QO breakers we put in as a safety measure.
One of these breakers is used exclusively to power an APC UPS, which we used to provide the power to our electronics equipment (computer, data acquisition electronics, sensors, etc.).
All of our equipment is DC powered, we use commercial power supplies to convert the AC to DC.
the only AC equipment is an air blower, which is on it's own branch with a GFCI breaker.
The cabinet and all of the equipment is grounded.
There are no external outlets.
We have a problem with the UPS, it is tripping the GFCI breaker when the UPS output power is off (battery discharged or intentionally disable output power).
We contacted APC and were told that the UPS exhibits leakage currents as a result of the common mode filters present within the UPS and the equipment connected to it.
We are now questioning ourselves about the need to have the GFCI breaker for the UPS, or just replace it with a regular breaker.
I've been reading the electric code and could not find a definitive answer.
I'm hoping to gain insight from your comments. Thank you.