does anybody can help me with this calculation.
how to calculate the general lighting load for a 2 story school building the dimention are 100 ft times 160.
to my understanding and based on an example that i found in a mike holt's book is
Lighting Load 3va ft2
so
100ft *160=16,000 va
16,000 va * 3 vaft2= 48,000 va
48,000va * 2 is based in 2 floors. = 96,000 this would be my result but i dont know if its right or not, does anybody out there can help or correct me, or whats the right way to do this calculation.
how to calculate the general lighting load for a 2 story school building the dimention are 100 ft times 160.
to my understanding and based on an example that i found in a mike holt's book is
Lighting Load 3va ft2
so
100ft *160=16,000 va
16,000 va * 3 vaft2= 48,000 va
48,000va * 2 is based in 2 floors. = 96,000 this would be my result but i dont know if its right or not, does anybody out there can help or correct me, or whats the right way to do this calculation.