I've run into this a few times in residential and am hoping to find a definitive answer to settle an argument (if there is a definitive answer).
I've run into a few houses wired just after 1965 with NM containing the safety ground that was properly bonded to the metal box, however, there were a few years where two-prong plugs were still the standard. When replacing said two-prong plug, is it necessary to connect a separate bonding pigtail from the new outlet (or switch) to the box, or is the metal-to-metal contact between the mounting tabs and the box a sufficient enough bond to satisfy code? It is electrically sufficient, but from everything I've found, there is a bit of a gray area in the code (if I'm not looking at it cross-eyed). And before anyone says it, yes, we know it's good practice to go ahead and bond it with a pigtail for redundancy.
Thanks,
Nick
I've run into a few houses wired just after 1965 with NM containing the safety ground that was properly bonded to the metal box, however, there were a few years where two-prong plugs were still the standard. When replacing said two-prong plug, is it necessary to connect a separate bonding pigtail from the new outlet (or switch) to the box, or is the metal-to-metal contact between the mounting tabs and the box a sufficient enough bond to satisfy code? It is electrically sufficient, but from everything I've found, there is a bit of a gray area in the code (if I'm not looking at it cross-eyed). And before anyone says it, yes, we know it's good practice to go ahead and bond it with a pigtail for redundancy.