Good day everyone,
As my previous problem on delta resistance computation has been solved. Big thanks!
We also have problem on resistance of a single heater, specifications are below:
P = 320W , V = 220V
Formula for getting its resistance is VxV/P = (220x200)/320 = 151.25ohms
We set a ±10% tolerance of resistance as a range for good heater condition.
However, upon actual reading of resistance using fluke, it gives a resistance of 182ohms which is more than ±10% of standard reading 151.25ohms.
Lowest -10% tolerance: 136.1ohms
Standard resistance: 151.25ohms
Highest +10% tolerance: 166.4ohms
This type of heater is spiral coil.
So here's my question, is our way of computing resistance if correct? Is our tolerance for judging a good heater is way to small? or is their any explanation why actual reading is far from computed resistance reading based on specs?
As my previous problem on delta resistance computation has been solved. Big thanks!
We also have problem on resistance of a single heater, specifications are below:
P = 320W , V = 220V
Formula for getting its resistance is VxV/P = (220x200)/320 = 151.25ohms
We set a ±10% tolerance of resistance as a range for good heater condition.
However, upon actual reading of resistance using fluke, it gives a resistance of 182ohms which is more than ±10% of standard reading 151.25ohms.
Lowest -10% tolerance: 136.1ohms
Standard resistance: 151.25ohms
Highest +10% tolerance: 166.4ohms
This type of heater is spiral coil.
So here's my question, is our way of computing resistance if correct? Is our tolerance for judging a good heater is way to small? or is their any explanation why actual reading is far from computed resistance reading based on specs?