Hi,
I am trying to recall the correct sizing requirements for the equipment conductors, Disconnect and HACR breaker on an outdoor A/C Unit. It's been a while since I have needed to calculate these.
The nameplate on the unit states:
208/230v 1 phase
Compressor RLA = 20.0
Compressor LRA = 150
Minimum Circuit Amps = 32.5
Maximum Fuse Amps = 50
Maximum Breaker Amps = 50
I must use the nameplate ratings for sizing if present based on article 440.
I also recall being allowed to use the 75 degree column of Table 310.16 for circuits below 100 amps provided all terminals of the circuit are rated at 75 degrees. Otherwise the 60 degree column would be used.
With terminals all rated at 75 degrees, I would need a minimum conductor size of #10 THHN given a minimum circuit amprage of 32.5. #10 THHN is good for 35 amps based on tables 310.16, 240.4(D) & 240.4 (G).
This would allow a minimum non fused disconnect rating of 30 amps and a HACR breaker of 50 amps based on maximum breaker size on nameplate to be used.
Am I correct in each part of my sizing calculations?
Thanks
I am trying to recall the correct sizing requirements for the equipment conductors, Disconnect and HACR breaker on an outdoor A/C Unit. It's been a while since I have needed to calculate these.
The nameplate on the unit states:
208/230v 1 phase
Compressor RLA = 20.0
Compressor LRA = 150
Minimum Circuit Amps = 32.5
Maximum Fuse Amps = 50
Maximum Breaker Amps = 50
I must use the nameplate ratings for sizing if present based on article 440.
I also recall being allowed to use the 75 degree column of Table 310.16 for circuits below 100 amps provided all terminals of the circuit are rated at 75 degrees. Otherwise the 60 degree column would be used.
With terminals all rated at 75 degrees, I would need a minimum conductor size of #10 THHN given a minimum circuit amprage of 32.5. #10 THHN is good for 35 amps based on tables 310.16, 240.4(D) & 240.4 (G).
This would allow a minimum non fused disconnect rating of 30 amps and a HACR breaker of 50 amps based on maximum breaker size on nameplate to be used.
Am I correct in each part of my sizing calculations?