GlennG
Member
- Location
- Hicksville, NY
I am having a little dispute with my co worker about sizing the conductors on a 36 kw Generac generator. He is saying 1/0 , i think 2/0 copper or 3/0aluminum.I went by this: 36000/240= 150amps x 1.25%= 187.5 amps. The generator has a 175 amp Breaker in it. Can anyone tell me if i am on the right track here?