Can someone help me make accurate sense of the following:
what is the best/easiest way to determine what "reactive" current there is on the input side of the UPS at that 60A input breaker, to know how much we're dealing with? The UPS manual says this model UPS has a power factor rating of greater than 0.8, and LAGGING, and an optional input filter can be purchased to increase pf to 0.9 or 0.93 which we do not have and are not sure if is worth looking into.
- I have a Liebert 80 kva UPS at work supplying a computer server room.
- it is 480v 3-phase input, and the same output
- On the UPS load side is a 480/208 transformer and distribution panel that wires some 20+ L6-30R receptacles in the server room
- There is a 60A main input breaker on the UPS input side
- is doing 480 x 60 = 28.8 kva accurate in determining the amount of power that could be drawn? if not please elaborate.
- I cannot make sense of the INPUT and LOAD numbers displayed on the UPS lcd panel...
- Input shows 44,44,45 when equipment on and mostly running
- Input will show 55,55,55 when running stress.exe on all computers to make them draw max power.
- Load numbers will show 19,25,33 when not at 100%, and around 25,31,40 when running stress.exe.
- I had been told the seemingly significant difference between the input and load numbers on the UPS panel was the result of reactive power because of current having to run around in the UPS capacitor banks.
- this UPS has 40 car size batteries in it and is 3 cabinets each the size of a large refrigerator to give you an idea.
- it is a double-conversion type... AC in, rectified to DC to charge batteries then inverted back to AC to clean/pure sine wave to the load.
- can someone elaborate on the input and load current numbers I am seeing on the UPS lcd panel and how to correctly use them to show total power being drawn? I don't get the 3 legs (3-phase) and how to correctly deal with that? Why are the input numbers almost always equal but the load numbers wildly different (i know why) but how do I add up or interpret the load current numbers to get a total power on the load side, to then compare to the input side? I see ~44 on the input and 19,25,33 on the load, all at 480v, that a significant difference no?
what is the best/easiest way to determine what "reactive" current there is on the input side of the UPS at that 60A input breaker, to know how much we're dealing with? The UPS manual says this model UPS has a power factor rating of greater than 0.8, and LAGGING, and an optional input filter can be purchased to increase pf to 0.9 or 0.93 which we do not have and are not sure if is worth looking into.