Koplinsky
New User
- Location
- Pennsylvania
- Occupation
- Estimator
I have a 1000A/3phase feeder that's called out to be 4 sets of [(3)#300, 2/0g, in 3" EMT)], copper.
My question is, according to table 310.15(B)(16), (1)#300 in column 75C has ampacity rating of 285. Why must I have 4sets of (3)300s, a total of 12, if (4)#300s provides 1140A. I am clearly reading this table wrong. Please help me understand.
My question is, according to table 310.15(B)(16), (1)#300 in column 75C has ampacity rating of 285. Why must I have 4sets of (3)300s, a total of 12, if (4)#300s provides 1140A. I am clearly reading this table wrong. Please help me understand.