Trawets
Member
- Location
- Pittsburgh
I'm running electrical for split a/c unit for a server room. The condensing unit will be above the drop ceiling in an adjacent room. It requires 277 vac which is available. The cooling unit will be in a server room requiring 208/230 vac, 13 fla on a separate circuit which the voltage is not available. The manufacture supplies a buck boost transformer (277 vac, 37.5 amp) which will be above a drop ceiling also. The part that I don't understand is the ocpd for the transformer and the cooling unit. My plan is from breaker to unit....40 amp breaker, #8 awg thhn wire to non-fused disconnect for transformer above ceiling, #8 awg thhn wire from transformer to fused disconnect on wall by cooling unit, 25 amp fuses with #10 awg thhn to the unit. I've read 450.4 for the last 3 days and I still think I have it wrong. So where and why am I wrong?:?