UltraMagneticAL
New member
I'm having a difficult time calculating what the induced voltage would be from three separate 3-Phase Underground 66kV Cables in Duct Bank on a group of control cables running parallel above the duct bank for approximately 100 meters.
So far, I've got some formulas to use:
Faraday's Law: Emf = -NΔϕ/Δt
Ampere's Law: Σ BΔl = μ̥ I for a straight conductor
where N = number of coils
ϕ = BA = magnetic flux
B = External Magnetic Field = (μ̥ I)/(2πr) [from Ampere's Law]
A = Area of Coil (for a wire, what do i substitute here?)
μ̥ = 4π * 10^-7 Permeability of Free Space (should I be using concrete? if so, what is it?)
Δl = infinitesimally small length of B
The 66kV duct bank will be buried 1m below the control cables.
When I used Faraday's Law to calculate the induced EMF I assumed 1 coil for N since it is a straight cable. Is this a correct assumption?
Any help or direction would be greatly appreciated!
Thanks,
Allen