Help wiring
Kevin.hndz
New york
Schneider electric PM5100 power logic need help wiring this up first time doing this need some help walking me through I've tried looking up diagrams but all seem to mark up v1 v2 v3 and such and this doesn't have anything like that where would the CT wired land and were does my 120v power land
What two wires are going to the display on the door? Looks like the red and the white (#10021 or #20071). You would need to provide 120 volts to those two wires to power the display. The neutral on VN or V and the line side of the two amp fuse for the hot leg.
Everything looks right to me. I seem to remember a problem with a fuse holder or a loose wire maybe. It was a solid 5 years ago. Check connections.
The 2 amp fuse is for powering the logic display. He'll need to figure out which of the neutrals #10021 or #20071 go along with the red conductor. The 120 volt hot goes to the line side of the fuse.
The neutral on the fuse appears to be with the circuit being monitored my guess is that goes on neutral block 'VN'.
The meter should be powered off an auxiliary power source that lands on the 2A fuse and the neutral block 'N'.
I dont see the auxiliary power source pulled in.
I missed that. 100%. I remember now. He needs to put the neutral on VN. And pull in the 120 voltw with the line on the 2a fuse, the neutral on the N and the Ground on the G to the right of the fuse block.
It would help if you had a wiring diagram for the panel that shows where their wire numbers go.