Running five 120v circuits with individual neutrals in wiremold 3000 for receptacle loads (battery chargers) using THHN. Looking at the table, I need to derate 50% for the ten CCC. According to the engineered plans, the connected load for each circuit is 1500va (12.5a). The circuits will be breakered at 20amps and run no further than 50' from the panel so voltage drop isn't an issue.
From the 90 degree column, I'm under the impression that I can still use #12 since it's rated at 30a so 50% of that would be 15a, which satisfies my 12.5a load. I can still put them on a 20a breaker as this demand doesn't effect the OCPD amapcity selection right? Am I doing the calculation correctly? Does the fact that they are all receptacles factor in?
The thing that is giving me pause is the plans call for all these circuits to be run in #8 (no type indicated) and it specifically says due to 310.15(B)(3). Does anyone know why this would be or what the engineer is including that I am not? Any help is greatly appreciated.
From the 90 degree column, I'm under the impression that I can still use #12 since it's rated at 30a so 50% of that would be 15a, which satisfies my 12.5a load. I can still put them on a 20a breaker as this demand doesn't effect the OCPD amapcity selection right? Am I doing the calculation correctly? Does the fact that they are all receptacles factor in?