I am installing a fused motor disconnect for a 10hp, 208 volt 3 phase motor.
The nameplate says it is 30.8 FLA with a locked rotor current of 179 amps.
430.103 commentary in the 2008 handbook says the disconnect shall be capable of interrupting the locked rotor current of the motor which I believe the fuses will take care of.
430.110 says that I need to size the disconnect at 115% of the FLA,
430.110.C (1) Says the rating of the disconnecting means shall be determined from sum of all currents at the full load condition and also at the locked rotor condition. But this is for Combination Loads which I dont believe applies to single motors.
Question #1- If I size the disconnect at 115% of the FLA andf make sure it is rated for the 10HP wouldnt that comply with code? (Which would be a 60amp disconnect using Time Delay Fuses rated at 15HP).
Question #2- Under what circumstance would we have to use the Locked Rotor Condition to size a disconnect?
If I had to use ther LRA at 179 amps my disconnect would have to be a 200 amp disconnect for a 30.8 amp load which seems crazy, I would like to know because next time it might be a disconnect for a combination load.
Thanks in advance for any input
The nameplate says it is 30.8 FLA with a locked rotor current of 179 amps.
430.103 commentary in the 2008 handbook says the disconnect shall be capable of interrupting the locked rotor current of the motor which I believe the fuses will take care of.
430.110 says that I need to size the disconnect at 115% of the FLA,
430.110.C (1) Says the rating of the disconnecting means shall be determined from sum of all currents at the full load condition and also at the locked rotor condition. But this is for Combination Loads which I dont believe applies to single motors.
Question #1- If I size the disconnect at 115% of the FLA andf make sure it is rated for the 10HP wouldnt that comply with code? (Which would be a 60amp disconnect using Time Delay Fuses rated at 15HP).
Question #2- Under what circumstance would we have to use the Locked Rotor Condition to size a disconnect?
If I had to use ther LRA at 179 amps my disconnect would have to be a 200 amp disconnect for a 30.8 amp load which seems crazy, I would like to know because next time it might be a disconnect for a combination load.