hi
this local race track called me to look at some problems there having with one area of the track lighting and the panel feeding these lights( breakers tripping, breakers burning up and finally the main breaker burned up). all the other lights of the track are feed from disconnect and are working fine. so the first step is a calculation 46, 1500watt halogen outdoor lights = 69000 va x 1.25 = 86250 va/240 volts = 360 amps. Does this look and sound right? it doesn't to me. if thats right each light will draw 6.25 amps? i would love to be able to look inside one of these light but there mounted on 65' poles. What they want to do is replace the existing 200 amp panel with a 225 amp panel and if my calculation are right this isn't going to help them at all. they will need a 400 amp service or turn off half there lights. any help or insights would greatly be appreciated thanks
this local race track called me to look at some problems there having with one area of the track lighting and the panel feeding these lights( breakers tripping, breakers burning up and finally the main breaker burned up). all the other lights of the track are feed from disconnect and are working fine. so the first step is a calculation 46, 1500watt halogen outdoor lights = 69000 va x 1.25 = 86250 va/240 volts = 360 amps. Does this look and sound right? it doesn't to me. if thats right each light will draw 6.25 amps? i would love to be able to look inside one of these light but there mounted on 65' poles. What they want to do is replace the existing 200 amp panel with a 225 amp panel and if my calculation are right this isn't going to help them at all. they will need a 400 amp service or turn off half there lights. any help or insights would greatly be appreciated thanks