On a new 100a residential service, MLO panel, can you reverse feed a 100a 2pole breaker as the main? I don't believe you can but i can't seem to find the answer
 
408.36(D) Back-Fed Devices. Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
 
Go to the catalog for the manufacturer of the panel and look under accessories. . .sometimes it gets real specific as to what the "fastener" is that will work for that make and model.
 
As to the OP yes I do it all the time.

I was going to post a thread similar to this.
With the new 310.15 -b (6) rule.

I have to replace a 150 amp meter base combo feed through panel.
As you may know they are rare in my area. So I would like to install a 200 amp feed through panel.
I will use 2/0 cu. from the meter to the 200 amp feed through panel.
There is a breaker for an ac/heat pump on the outside panel.

Then the existing inside panel has a 150 amp main breaker.

So my question is, would I still be able to use the 2/0 copper to the 150 amp main?
The panel would be protected from overload by the 150.
The 2/0 it seems also would be protected from overload by the 150.
 
Welcome to the site with 10 post you have not learned yet, but there may be quick questions but there are seldom quick answers to those questions.
 