A multi unit apt
Building feed grounded neutral
After meter 3 wire feeds (no gnd) feeds to apt panel
Apt panel neutral is grounded.


Why is this dangerous?????
Line to line fault breaker trips
Line to neutral breaker trips
Receptacle Outlet box hot falls off hits metal case, gnd on NM cable brings current to panel, from panel neutral completes circuit breaker trips

I am sure I somehow am missing something help please. Yes I work nights lol

Dave
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A multi unit apt
Building feed grounded neutral
After meter 3 wire feeds (no gnd) feeds to apt panel
Apt panel neutral is grounded.
Assuming that the meters feed the panels which contains the service disconnects there is nothing that is dangerous. That is normally how the service would be wired. There would be no EGC's ahead of the service disconnects.
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Hopefully the “grounded neutral” meant by a GEC. Also after panel hopefully no 3 wire 120 V loads with a bootleg EGC. As Tom stated also depends on type of raceway.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
The reasoning behind four wires past the service disconnect is if the neutral became disconnected for some reason, such as a bad connection, everything grounded by it becomes “hot”. It can happen on the utility side too, but the code writers decided for practicality to just start it at the service disconnect. Same as old three wire dryer and range receptacles. Cost of extra wire exempted those for a long time. Sure, the likelihood of the neutral becoming open is low, but that is the reasoning behind it.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Does each apt have a service disconnect, if so where?
What type raceway between meter and apt panel?
In basement each apt has fused disconnect. No raceway after disconnect 3 wire SE.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Assuming that the meters feed the panels which contains the service disconnects there is nothing that is dangerous. That is normally how the service would be wired. There would be no EGC's ahead of the service disconnects.
After meter fused disconnect 3 wire SE leaves no gnd
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Hopefully the “grounded neutral” meant by a GEC. Also after panel hopefully no 3 wire 120 V loads with a bootleg EGC. As Tom stated also depends on type of raceway.
Main building feed terminates in a fused disconnect. Neutral is connected to grounding electrode system there.

Several meters are connected together via wire way and rigid till after meter wires connect to fused disconnect in basement 60amp and from there transitions to SE cable no Raceway to a main lug panel
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
The reasoning behind four wires past the service disconnect is if the neutral became disconnected for some reason, such as a bad connection, everything grounded by it becomes “hot”. It can happen on the utility side too, but the code writers decided for practicality to just start it at the service disconnect. Same as old three wire dryer and range receptacles. Cost of extra wire exempted those for a long time. Sure, the likelihood of the neutral becoming open is low, but that is the reasoning behind it.
Thank you the problem is an entire apt for elderly is affected I’m trying to find them an out.
I need to get deeper into your reasoning I don’t 100% understand
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
The "out" is whether the installation was compliant when installed.
About 1955 no original diagram.
Building had a fire 12 of 84 units will get complete rewire.
Other units federal pacific boxes they need replaced but can’t pass inspection with 3 wire some of the boxes look like this ugh
 

Attachments

  • IMG_6727.jpeg
    IMG_6727.jpeg
    430.7 KB · Views: 7

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician

Attachments

  • IMG_6891.jpeg
    IMG_6891.jpeg
    65.9 KB · Views: 4

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Thank you the problem is an entire apt for elderly is affected I’m trying to find them an out.
I need to get deeper into your reasoning I don’t 100% understand
Think “open neutral”, the loads will try to find an alternate path back to the source. Which can be a person touching something that bonded to the neutral. This only happens if the neutral is compromised. Extreme voltage drop can also cause voltage potential, usually from appliances to metallic water systems that have been bonded at the entrance.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Does each apt have a service disconnect, if so where?
What type raceway between meter and apt panel?
Tom looks a lot like this but no conduit between disco and panel
Might need to insulate the Nuetral on the SE cable. Run this by your AHJ before though.
the neutral is currently insulated so that’s good. I was currently thinking like you were with the ground but see the pic I think it’s no bueno
 

Attachments

  • IMG_6898.jpeg
    IMG_6898.jpeg
    350.3 KB · Views: 5
  • IMG_6901.jpeg
    IMG_6901.jpeg
    320.7 KB · Views: 5

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Tom looks a lot like this but no conduit between disco and panel

the neutral is currently insulated so that’s good. I was currently thinking like you were with the ground but see the pic I think it’s no bueno
That's for new installations. It's still permissible to add a ground after the fact atleast for branch circuits. Look at 250.130
 