Hello i am struggling to verify if my proposed controls options will work.
If a class room has three rows of lighting with a dedicated switch for each, Can i install one rLSXR (cutsheet attached) knockout mount sensor on each row to control the lighting?
EC says that this will not work and is supposed to be installed for individual light fixtures and not for a row of lighting. Acuity confirmed that this can work for a zone of light fixtures. I was thinking this can be installed on the edge of the row with incoming power and that way it can interrupt the flow to turn off the lights on vacancy. Picture for reference.
Any advise is appreciated. Thankyou
If a class room has three rows of lighting with a dedicated switch for each, Can i install one rLSXR (cutsheet attached) knockout mount sensor on each row to control the lighting?
EC says that this will not work and is supposed to be installed for individual light fixtures and not for a row of lighting. Acuity confirmed that this can work for a zone of light fixtures. I was thinking this can be installed on the edge of the row with incoming power and that way it can interrupt the flow to turn off the lights on vacancy. Picture for reference.