Background info:
We are in the process of rewiring a transformer that will be backfed for experimental work here at the office. I was initially tasked with providing a variable voltage system from 0-8000VAC. The setup was a 14kVa variac capable of 0-280VAC coupled with a backfed pole mount transformer(see below nameplate).
The two hot lines out of the variac were wired across x1 and x3, with x2 left floating. This system worked as intended with no issues and we were able to use a full 40A(measured on the LV side) @ 8kV without issue.
After some testing it was discovered that our initial data was not correct, and we would need upwards of 12kV to continue. On a budget, and not wanting to purchase a new variac to feed the pole transformer 480/redo the breaker and disconnect done by the electrician, we purchased a surplus pad mount tranformer(see below nameplate).
Current Problem:
There was a learning curve when the new transformer showed up, as no one here has any experience with distribution transformers(I'm hoping the mistake/fault lays somewhere here). I learned about, then purchased, loadbreak elbows, a bayonet fuse, and rented a crimper to get it wired up. Once wired up in the same way as the previous unit (voltage accross x1 and x3, with the grounding strap to x2 removed) we get nothing. When an oscilloscope probes the output side the high voltage is present, but placing a load across it yields nothing. The only conclusion we could draw from that is we are picking up the noise from the coils.
I would love to get some input on anything that could be causing this behavior. One thing is that the diagram shows a fuse inline with a fuse in a holder, but I could only find the place for the bayonet fuse.
Thanks, Sam
We are in the process of rewiring a transformer that will be backfed for experimental work here at the office. I was initially tasked with providing a variable voltage system from 0-8000VAC. The setup was a 14kVa variac capable of 0-280VAC coupled with a backfed pole mount transformer(see below nameplate).

The two hot lines out of the variac were wired across x1 and x3, with x2 left floating. This system worked as intended with no issues and we were able to use a full 40A(measured on the LV side) @ 8kV without issue.
After some testing it was discovered that our initial data was not correct, and we would need upwards of 12kV to continue. On a budget, and not wanting to purchase a new variac to feed the pole transformer 480/redo the breaker and disconnect done by the electrician, we purchased a surplus pad mount tranformer(see below nameplate).

Current Problem:
There was a learning curve when the new transformer showed up, as no one here has any experience with distribution transformers(I'm hoping the mistake/fault lays somewhere here). I learned about, then purchased, loadbreak elbows, a bayonet fuse, and rented a crimper to get it wired up. Once wired up in the same way as the previous unit (voltage accross x1 and x3, with the grounding strap to x2 removed) we get nothing. When an oscilloscope probes the output side the high voltage is present, but placing a load across it yields nothing. The only conclusion we could draw from that is we are picking up the noise from the coils.
I would love to get some input on anything that could be causing this behavior. One thing is that the diagram shows a fuse inline with a fuse in a holder, but I could only find the place for the bayonet fuse.
Thanks, Sam