tjacobs
Member
- Location
- Moorestown, NJ
I have a customer who is installing a rooftop air conditioning unit. Because of the corrosive environment of the plant and plant specs the conduit needs to be schedule 80 PVC. The AC unit comes with a 400 amp disconnect switch with 350 amp fuses. AC unit requires 480 volt 3 phase. The conduit run will be on the roof on 5" high support blocks. The run is 470' long. I found with NEC 310.15 B 3 there is an exception that says I can use XHHW-2 insulation and I do not need to apply the adjustment Factor for being on a rooftop. I am confused on weather I need to factor in ambient temperature and how to apply this adjustment if needed. Looking for some guidance. Any help would be appreciated.
Thanks.
Thanks.