Help with compact AL RHH/RHW

Status
Not open for further replies.

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
When sizing conduit for USE-2 alumaflex compact AL RHH/RHW do you just use the standard RHH/RHW sizing (example Ch9 table 10)?

The reason I ask is because according to table C.10A I could get 5 #2 compact wires into a 1-1/4" PVC but with table C.10 only 4 #2 RHH/RHW wires (non compact) in the same conduit...

So this wire claims it's compact but none of the tables list any RHH/RHW wires that are compact....
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
twoskins, read any note two in those tables.

:confused: I guess I'm gonna need you to spell out the connection that would explain the compact issue...


2. Two-hour fire-rated RHH cable has ceramifiable insulation which has much larger diameters than other
RHH wires. Consult manufacturer?s conduit fill tables.
*Types RHH, RHW, and RHW-2 without outer covering.
 

480sparky

Senior Member
Location
Iowegia
Compact conductors are the same ampacity as non-compacted, compressed or solid. It's only used for raceway fill purposes.

CompactConductors.jpg


You may need to contact the manufacturer to find out the conductor properties.
 