Hello Everyone,
I've been asked to run power for an elevator. If anyone could help me with the calculations I would really appreciate it.
Power is 208 volt 3 phase.
Motor HP is 25
Starting A/C amps is 236
Total (Full load motor) A/C amps is 114
Rated A/C amps is 78.7
Short circuit current rating (At 600v) is 5000 amps
I've come up with these calculations
FLC x 140%
114 x 1.4=159.6 amps for wire size
OCPD
78.7 amps x 250%=196.75 amps
Which size and type of fuses and disconnect should I use? Are my calcs correct?
Hate to burn them, but Thyssen Krupp will not offer any info besides the short paragraph above.
Your help will be much appreciated!!!!
I've been asked to run power for an elevator. If anyone could help me with the calculations I would really appreciate it.
Power is 208 volt 3 phase.
Motor HP is 25
Starting A/C amps is 236
Total (Full load motor) A/C amps is 114
Rated A/C amps is 78.7
Short circuit current rating (At 600v) is 5000 amps
I've come up with these calculations
FLC x 140%
114 x 1.4=159.6 amps for wire size
OCPD
78.7 amps x 250%=196.75 amps
Which size and type of fuses and disconnect should I use? Are my calcs correct?
Hate to burn them, but Thyssen Krupp will not offer any info besides the short paragraph above.
Your help will be much appreciated!!!!