Help with my wiring diagram running 400/230v three phase

Need help with my diagram, is neutral and ground bonded at my panel here?
Meter base is 130m away from my 50AT panel.
I'd say no since the plans say your originating from existing meter center distribution panelboard.
Last I checked the Philippines follows its IECitized version of the NEC (in your code its 2.50.2.5 ) there is one main bonding jumper at the first main panel (TN-C-S ) and after that your basically a TN-S system.
 
I'd say no since the plans say your originating from existing meter center distribution panelboard.
Last I checked the Philippines follows its IECitized version of the NEC (in your code its 2.50.2.5 ) there is one main bonding jumper at the first main panel (TN-C-S ) and after that your basically a TN-S system.
In picture 2/2 do i need to ground rod the neutral and separate it from Ground?
 
In picture 2/2 do i need to ground rod the neutral and separate it from Ground?
Your neutral would be floating in the panel, no ground rod attached, so delete that.
Presumably your panel 130m (427') away from the service is in a separate structure so you would need establish a grounding electrode system for that building and connect that to your your equipment ground bar. (2.50.2.13)
 
Your neutral would be floating in the panel, no ground rod attached, so delete that.
Presumably your panel 130m (427') away from the service is in a separate structure so you would need establish a grounding electrode system for that building and connect that to your your equipment ground bar. (2.50.2.13)
I will use it for single phase single pole loads 230V L-N neutral, im confused why is the diagram neutral attached to a ground rod.
 
I am curious, this is in the Philippines? What sort of transformer is it, a shared three phase core? Do they ground anything on the utility side? Thanks!
 
I am curious, this is in the Philippines? What sort of transformer is it, a shared three phase core? Do they ground anything on the utility side? Thanks!
I cant speak to the transformer core, last I checked the Philippines is on a TN-C-S system, where the utility side up to the first means of disconnect is TN-C or Multi Grounded Neutral (MGN) then neutral and protective earth are separate after the first means of (service) disconnect on customer side. The modified version of NFPA 70 National Electrical Code (NEC) they adopt has not many if any changes to the sections on grounding what we in the US call article 250, the main change to the NEC is they change every occurance of 120V to 230V, so a single phase utility transformer in a residential area would be grounded on one end unlike here where we center tap.
A TN-C system like the OP was asking about is prohibited on the customer side.

Now your turn how does Paraguay work?
 
In Paraguay, all homes have a floating neutral that is sometimes connected to the utility's "ground," but not always. They use 23 kV delta, with a small neutral at the top for lightning and drain on shielded cables. Most homes have three phase 380/220 50 Hz, with the exception of small shacks, where a single phase service up to 40 A is provided (the limits without special approval are 10 kW for single phase and 30 kW for three phase based on 220 V). 220 V is the regulation, but they are always 400/231 transformers being used.

However, large buildings like apartment buildings and malls, where there are many separate meters (which measure neutral, by the way -- four wires in and four out), have a proper TN-S system. A little icon on the LCD comes on if any neutral current was bypassing through the meter somehow (e.g. to the communal ground if it exists or leaking to a neighbor's connection).

The risk is mitigated by installing a 30 mA RCD in newer homes, but in old homes, your bets are off.
 